Cable length questions

A catch-all category for LED-related questions, content, news, rumors, or whatever. If it doesn’t fit elsewhere, put it here.
Post Reply
Fat Freddy's Cat
LED-Curious
LED-Curious
Reactions:
Posts: 9
Joined: Mon Aug 05, 2019 7:53 pm

Hi there folks

Couple of I hope easy questions

I want to keep my drivers in a seperate room to my work area.

I will only need to run cable an absolute maximum of 8 metres (25ft)

Two types of cable

1. Power output from my MW320H-C1400B @ 200W to 4xQB288 and MW240-C1750B @ 210W to 6xQB120
2. Potentiometer cable from above also.

The lights themselves are wired with 18AWG solid cable - and on a short run this is also used for both power and potentiometer connections (each being about 5 feet max)

Am I ok to run the same cable up to 25 feet? Or should I be looking for something thicker? I'm guessing yes with the potentiometer as I assume there is fuck all current passing through it - but with the power line do I need to upgrade to thicker/shielded cable?

Thanks for any advice.
Shimbob
LED Wizard
LED Wizard
Reactions:
Posts: 642
Joined: Mon Nov 27, 2017 11:29 pm

If I tell you, will you promise not to shit in my shoes? :)
Shimbob
LED Wizard
LED Wizard
Reactions:
Posts: 642
Joined: Mon Nov 27, 2017 11:29 pm

Check out a Voltage drop calculator. Nothing wrong with 25' of 17AWG, which is what the MW320 has.
You're lucky that your voltage is already pretty high, as higher voltages and lower amps tolerate longer wire runs better than lower volts & high amps.
Fat Freddy's Cat
LED-Curious
LED-Curious
Reactions:
Posts: 9
Joined: Mon Aug 05, 2019 7:53 pm

Found this https://www.solar-wind.co.uk/info/dc-ca ... calculator

It jumps at the 4 meter mark - am I right to assume it would be a gradual drop rather than a defined one?

I totally won't shit in your shoes.
Shimbob
LED Wizard
LED Wizard
Reactions:
Posts: 642
Joined: Mon Nov 27, 2017 11:29 pm

Voltage drop is constant per unit length of wire and proportional to the length of the wire, ie there shouldn't be any change in rate of drop over length.

I think anything that at least matches the 17awg out of the driver or larger size will do fine. I run 10awg because the spool was only a couple bucks more than 14awg.